Calculating total energy gain/loss due to ventilation air

asked 2022-11-30 17:22:19 -0500

willyJohan's avatar

updated 2022-12-01 10:17:03 -0500

I am trying to find out how much of a building's heating or cooling loads are due to ventilation air. Is there a specific variable, meter or summary report for this? if not, are the following variables:

  • Air System Outdoor Air Mechanical Ventilation Requested Mass Flow Rate
  • Zone Air Temperature
  • Site Outdoor Air Drybulb Temperature

the correct ones to use with with good old ṁ x Cp x dT?

Thanks.

edit retag flag offensive close merge delete

Comments

What EnergyPlus object are you using to model ventilation?

shorowit's avatar shorowit  ( 2022-12-01 08:21:07 -0500 )edit