Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Is there a way of modeling fixed outdoor air fraction for VAV systems in CBECC-Com?

asked 2015-06-05 08:08:52 -0600

My hunch is that this is only possible through the Exceptional Design Compliance process, but I just wanted to see if there was a way of doing this within CBECC-Com.

I'm looking to model fixed outdoor air fraction for a system that varies supply airflow (the design OA is greater than the minimum required). My assumption is that CBECC-Com defaults to providing the design outdoor air at all times regardless of the supply airflow rate.

edit retag flag offensive close merge delete

Comments

I'm going to try to use the Scheduled option for the Outside Air Control Schedule Method input and set the min fraction sch to be the outdoor air fraction.

anchapin's avatar anchapin  ( 2015-06-05 08:24:07 -0600 )edit

After adding the min fraction schedule, I found out that this Outside Air Control Schedule Method is not allowed for compliance analysis simulations.

anchapin's avatar anchapin  ( 2015-06-05 12:59:07 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2015-06-05 12:59:37 -0600

This appears to not be an allowed input for compliance analysis.

edit flag offensive delete link more

Comments

Yes, you are correct, CBECC does not currently support modeling fixed OA fraction systems. If you feel that this capability is important, I recommend submitting an 'Other' issue and specify it as a feature request: http://bees.archenergy.com/issue.html This will allow us to formally track it as a possible feature for future versions.

DavidReddy's avatar DavidReddy  ( 2015-06-05 19:08:49 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2015-06-05 08:08:52 -0600

Seen: 206 times

Last updated: Jun 05 '15