Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Manually specified airflow is "ignored"

asked 2022-10-20 10:57:50 -0500

Jim Dirkes's avatar

updated 2022-10-20 15:53:42 -0500

I'm scratching my head! I've specified a very simple, electric heating-only system with heat exchanger to be constantly at 6.6m3/s (14,000 cfm). The IDF confirms this value in several locations. (AirLoopHVAC, HeatExchanger:AirtoAir:SensibleandLatent, Fan:Constantvolume)

When I run the simulation, however, and examine the output, the airflow shows a constant 4.6m3/s (~9,800 cfm).

If I change the inputs to 9.9m3/s (21,000cfm), the results stay at 4.63m3/s.

This makes no sense to me, since I think I've manually specified everything associated with airflow... Insights will be very much appreciated.

edit retag flag offensive close merge delete

Comments

Can you attach your IDF via e.g. Google Drive or Dropbox? I doubt anyone can help without more information.

shorowit's avatar shorowit  ( 2022-10-20 18:13:29 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2022-10-21 08:13:19 -0500

Jim Dirkes's avatar

I was reminded of something I "learned" several months ago by Shaun Wang at DesignBuilder: If I autosize AirDistributionUnits (ADU), but hard size the fan airflow... the hard sized fan airflow is ignored whenever the autosized ADUs need a smaller total.

Manually sizing the ADUs corrects that problem.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2022-10-20 10:57:50 -0500

Seen: 508 times

Last updated: Oct 21 '22