I find a severe error in energy plus and don't understand it!
I am getting the error from "Errors" button but don't know what they mean and how to solve them:
** Severe ** FindRootSimpleController: Controller error for controller = "Big Room COOLING COIL CONTROLLER"
** ~~~ ** Environment=RUN PERIOD, at Simulation time=03/06 14:30 - 14:40
** ~~~ ** Controller function is inconsistent with user specified controller action = Reverse action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature setpoint = 13.74 [C]
** ~~~ ** Controller sensed temperature = 13.74 [C]
** ~~~ ** Controller actuator mass flow rate set to 17.02 [kg/s]
** ~~~ ** Controller actuator temperature = 7.00 [C]
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature
** ~~~ ** Note: Hot water coils should be normal action and the entering hot
** ~~~ ** water temperature (controller actuator temperature) should be above the setpoint temperature
1.I have set the plantloop Availability Manager so the cooling coil don`t work On March 6.
2.The controller action=Reverse and I simulate the idf document when I change the controller action=Normal but the error did not change.
Thanks a lot!