How do you model exhaust fans in OpenStudio

asked 9 years ago

tajjmann's avatar

updated 9 years ago

I am developing a model of commercial building and as party of the equipments in the building are Exhaust Fan. Any idea on how to model this?

Preview: (hide)

2 Answers

Sort by » oldest newest most voted
8

answered 9 years ago

Add the ZoneHVAC:FanZoneExaust object to the zones. This can be done by finding the Zone Exhaust Fan in the library through the Thermal Zones tab.

Preview: (hide)
link

Comments

1

Thanks Mathew I figured but I still have a problem. The room i intend to model is empty as such no need to add a thermostat. However model would not run without one. Any idea?

tajjmann's avatar tajjmann  ( 9 years ago )

Just add cooling and heating setpoints to the zone(s) to overcome the errors and then make sure they're unoccupied to keep the unmet hours down.

MatthewSteen's avatar MatthewSteen  ( 9 years ago )
1

Or widen the deadband for the heating cooling thermostat schedules to prevent unmet hours.

Kyle Benne's avatar Kyle Benne  ( 9 years ago )

This was an OS issue that has been fixed.

MatthewSteen's avatar MatthewSteen  ( 9 years ago )
4

answered 9 years ago

An important note from the Input Reference Guide for Fan:ZoneExhaust

The way in which the exhaust fan impacts central air system can be controlled by declaring what portion of the flow has been balanced by simple airflow from infiltration, ventilation, or mixing. However it is important to note that presence of an exhaust fan does not by itself drive any simple airflow such as infiltration, ventilation, or zone mixing. There is no comprehensive automatic mass balancing between air system flows, exhaust flows, and the separate simple airflows. For balancing, the simple airflows need to have their own input objects that need to be coordinated with the exhaust fan.

Preview: (hide)
link

Comments

We also support Zone Ventilation Design Flow rate in OpenStudio now, but not in the GUI, so need a measure to add them. This is a simple ventilation object that brings outdoor air directly into a zone and depending on ventilation type (Natural, Exhaust, Intake, or Balanced) it can add fan consumption and heat gain form fan to intake air.

There is a simple add zone ventilation design flow rate measure that just has the fan scheduled. A more advanced example, fan assist night ventilation, reacts to outdoor air temperature.

David Goldwasser's avatar David Goldwasser  ( 9 years ago )

I see the object "Zone Ventilation Design Flow Rate" in the GUI right now (haven't tried it). OS 10.1.1

Julien Marrec's avatar Julien Marrec  ( 9 years ago )
1

Good catch, my mistake, I didn't realize it made it into GUI. Thanks @Kyle Benne. ZoneMixing isn't in I don't think? I think was more complex design.

David Goldwasser's avatar David Goldwasser  ( 9 years ago )

That means to simulate natvent, the sum of "Fan:ZoneExhaust" , natVent airflow and infiltration should sum 0?

JuanPablo's avatar JuanPablo  ( 4 years ago )