Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

CondFD Surface Temperature Node not showing

asked 2022-09-27 22:23:57 -0500

hj's avatar

updated 2022-09-28 09:28:52 -0500

I am simulating an EnergyPlus model with PhaseChangeHysteresis object.

Based on the RDD file it says that I can report "CondFD Surface Temperature Node" for nodes 1 to 29. However, for a specified exterior wall (which include PCM), the output table reports nodes 1 to 20 and not 29. other surfaces like a ceiling, (without PCM) it shows all temperature nodes from 1 to 29. I appreciate any help.

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
0

answered 2022-09-29 07:30:40 -0500

GR@VT's avatar

The number of nodes that are reported for each construction depends on the thermal diffusivity of the materials (α) used in the same and I assume not all of your constructions will be the same. If you read out the variables with higher node numbers for all surfaces (please note that I refer to model planes as "surfaces" here, and not the surface of a construction itself), you will see which ones are divided into more elements.

edit flag offensive delete link more

Comments

Thank you for your response! I have seen two walls beloning to the same construction (exterior walls) one with only one node and the other is with 20 nodes. Any clues?

hj's avatar hj  ( 2022-09-29 14:36:05 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2022-09-27 22:23:57 -0500

Seen: 72 times

Last updated: Sep 27 '22