Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0

asked 2022-08-29 08:31:24 -0600

ecroftFoE's avatar

updated 2022-08-30 09:03:22 -0600

Hello,

I have read through the other posts that are related to this error and am still unable to fix my error. I am brand new to OpenStudio, so I am unsure of how to continue with my simulation. I'm working on the severe errors before I work through the warning errors. The only error I am receiving is below.

* Severe * PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-0.52081]. * ~~~ * pb =[98088.00], tdb=[-914.65], w=[1.4285632E-002]. * ~~~ * Routine=CorrectZoneHumRat During Warmup, Environment=EAU_CLAIRE ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:00 - 01:00

I have natural gas fired furnaces with exhaust fans for each thermal zone, I do not have the furnaces autosized. They are 80% efficiency at 80,000 btu/h. I am just trying to establish a baseline for a small office before working with higher efficiency equipment. When running my simulation I currently have the OS measure surface matching and Energy+ measure add output diagnostics. Am I missing anything to just run a basic energy evaluation on a building?

I'm new so I cannot upload documents as of yet. I can send the error document and photo if needed. Thank you in advance.

Evan

edit retag flag offensive close merge delete

Comments

1

@ecroftFoE instead of uploading documents & photos, you can store them on Google Drive, Dropbox, etc. and then share the URL to those files in your post here on Unmet Hours.

Aaron Boranian's avatar Aaron Boranian  ( 2022-08-30 09:04:17 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2022-08-30 09:03:38 -0600

This type of warning, where tdb=-914.65 C, typically means the zone is not getting heated. You might add reporting during warmup and reports (output:variable) for the zone temp and furnace performance to see why the zone does not get heated.

Output:Diagnostics, ReportDuringWarmup;

Output:Variable,*,Zone Mean Air Temperature,hourly;

Output:Variable,*, something showing how your equipment is operating , hourly;

See the rdd file for available output report variables.

edit flag offensive delete link more

Comments

Thank you for this answer. This prompted me to go deep into all my HVAC to make sure everything had the proper schedules and setpoints. I was missing the heating schedule on one of my thermal zones. I successfully got a full simulation to run this morning, and can now start adding in different measures and parameters. Thanks again!

ecroftFoE's avatar ecroftFoE  ( 2022-09-01 09:35:37 -0600 )edit