Dehumidification issue (Water Cooled System, DesignBuilder)

asked 2022-07-04 14:20:51 -0500

Debayan93's avatar

Hi,

I am using a VAV reheat Water-cooled chiller with full humidity control template in Detailed HVAC mode (DesignBuilder version 6) as shown below. However, I couldn't achieve the RH between the setpoint range (35%-60%) when my temperature setpoints are (13 and 22 °C) which are some operational boundary conditions. For my requirement (annual average temp 18 °C and RH 50%), I can increase the heating setpoint temperature a bit more (15-16 °C). However, I am trying to understand due to which possible reason/s the dehumidification are not happening accordingly or this might be a limitation for such system.

For this simulation, I kept all the values either autosize or pre-loaded based on template.

I have attached the model for any reference, https://we.tl/t-Bc8EvDY8MU. Any insight will be highly appreciated.

HVAC

T&RH

Best regards,

Debayan

edit retag flag offensive close merge delete

Comments

@Debayan93 is your plot of temperature and relative humidity for the whole building? If so, that is averaging for all zones in the model, including the unconditioned ones.

Aaron Boranian's avatar Aaron Boranian  ( 2022-07-05 09:03:31 -0500 )edit

Hi @Aaron Boranian, currently my model has only one zone which is conditioned by the AHU. So the plots will be practically the same.

Debayan93's avatar Debayan93  ( 2022-07-05 10:38:55 -0500 )edit