asked 2022-06-24 12:06:13 -0500

kbk78's avatar

Is there a listing of coils allowed in a central air loop. I am trying replace the HW and CHW coil with:

Coil:Heating:WaterToAirHeatPump:EquationFit

Coil:Cooling:WaterToAirHeatPump:EquationFit

But I get this error.

  ** Severe  ** GetAirPathData: AirLoopHVAC = "SYS1".
  **   ~~~   ** ..Invalid Air Loop Component Type = "COIL:HEATING:WATERTOAIRHEATPUMP:EQUATIONFIT".
  **   ~~~   ** ..Air Loop Component Name = "SYS1 WHPH HEATING COIL".

What alternatives do I have if I want to model WaterSource HP coils in a DOAS system.

There appears to be a similar unresolved question echoed here question.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2022-10-10 16:12:02 -0500

You are experiencing a limitation for what EnergyPlus objects can be used to contain various coils and fans on the supply branch of a central air system. This limitation is shown in the first table of the Unitary Equipment Group documentation of the Input Output Reference.

If you are seeing this severe error, it is likely because you are assigning the water-to-air heat pump cooling/heating coils that you want to use directly to the Branch object. Seeing the vertical columns for these coils in the table, that is not allowed (no "X" for the first row labeled AirLoop HVAC Main Branch). Instead, you would look for a unitary option that DOES have an "X" in it's row: