Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Humidistat setting in Energyplus using HVAC Templates : Fan Coils

asked 2022-06-07 23:12:40 -0500

Donner's avatar

updated 2022-06-08 09:13:56 -0500

Hi. Im using Energyplus. I wanna setting humidistat in energyplus. However, im using Fan Coils HVAC system. at the first im using HVACTemplates:FanCoil. I need to keep the RH between 60-70 % and Temperatures 23-25 C.

Please anyone help me thanks.

Here my HVACTemplates:FanCoil Code

HVACTemplate:Zone:FanCoil,
Gudang RM,               !- Zone Name
RM 03 Target 23-25,      !- Template Thermostat Name
3,                       !- Supply Air Maximum Flow Rate {m3/s}
,                        !- Zone Heating Sizing Factor
,                        !- Zone Cooling Sizing Factor
Flow/Person,             !- Outdoor Air Method
0.00944,                 !- Outdoor Air Flow Rate per Person {m3/s}
,                        !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
,                        !- Outdoor Air Flow Rate per Zone {m3/s}
Infiltration 2,          !- System Availability Schedule Name
0.8,                     !- Supply Fan Total Efficiency
1618.8,                  !- Supply Fan Delta Pressure {Pa}
0.8,                     !- Supply Fan Motor Efficiency
1,                       !- Supply Fan Motor in Air Stream Fraction
ChilledWater,            !- Cooling Coil Type
Infiltration 2,          !- Cooling Coil Availability Schedule Name
10,                      !- Cooling Coil Design Setpoint {C}
HotWater,                !- Heating Coil Type
,                        !- Heating Coil Availability Schedule Name
50,                      !- Heating Coil Design Setpoint {C}
,                        !- Dedicated Outdoor Air System Name
TemperatureDifference,   !- Zone Cooling Design Supply Air Temperature Input Method
20,                      !- Zone Cooling Design Supply Air Temperature Difference {deltaC}
SupplyAirTemperature,    !- Zone Heating Design Supply Air Temperature Input Method
0,                       !- Zone Heating Design Supply Air Temperature Difference {deltaC}
,                        !- Design Specification Outdoor Air Object Name
,                        !- Design Specification Zone Air Distribution Object Name
,                        !- Capacity Control Method
0.33,                    !- Low Speed Supply Air Flow Ratio
0.66,                    !- Medium Speed Supply Air Flow Ratio
Infiltration 2,          !- Outdoor Air Schedule Name
Electric,                !- Baseboard Heating Type
Infiltration,            !- Baseboard Heating Availability Schedule Name
0;                       !- Baseboard Heating Capacity {W}

Thanks for your Help!!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2022-06-08 13:16:31 -0500

The fan coil model does not include humidity control. I suggest changing to one of the other ZoneHVAC equipment types that does allow humidity control. For example HVACTemplate:System:Unitary can control humidity.

edit flag offensive delete link more

Comments

okey thanks sir for your Info!!

Donner's avatar Donner  ( 2022-06-09 04:45:17 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2022-06-07 23:12:40 -0500

Seen: 222 times

Last updated: Jun 08 '22