How to add HeatExchanger:AirToAir:SensibleAndLatent with Supply Air Outlet Temperature Control to AirLoopHVAC:DedicatedOutdoorAirSystem
I want to add HeatExchanger:AirToAir:SensibleAndLatent
to AirLoopHVAC:DedicatedOutdoorAirSystem
, but I have a problem. Let me explain using an ExampleFile SmallOffice_CentralDOAS.idf. I added HeatExchanger:AirToAir:SensibleAndLatent
as illustrated below. Here is the revised idf file (V9-6-0). One more revision is that originally the OA Supply Fan was located in front of the heating coil i.e, blow-through configuration, but the Fan was changed after the cooling coil i.e., draw-through configuration.
When I set Supply Air Outlet Temperature Control
of HeatExchanger:AirToAir:SensibleAndLatent
to "No", there is no error and the simulation completes sucsessflly. However, when I set Supply Air Outlet Temperature Control
to "Yes", the following severe error occurs and the simulation terminates even though I add a temperature setpoint with SetpointManager:Scheduled
.
** Severe ** Missing temperature setpoint for HeatExchanger:AirToAir:SensibleAndLatent "HEX" :
** ~~~ ** use a Setpoint Manager to establish a setpoint at the supply air outlet node of the Heat Exchanger.
** Fatal ** Previous condition causes program termination.
At first, the same error occurred in another energy model which was much more complecated, so I tested with the simple ExampleFile to clarify the cause.
I tried several things such as adding OutdoorAir:Mixer
and Controller:OutdoorAir
which are usually not required for AirLoopHVAC:DedicatedOutdoorAirSystem
. I also tried changing SetpointManager:Scheduled
to SetpointManager:MixedAir
, but they were all in vein. Any suggestions?
I forgot to share my idf files. They are here. The version is V9-6-0.
Still waiting for any advices. I cannnot enable
Supply Air Outlet Temperature Control
ofHeatExchanger:AirToAir:SensibleAndLatent
.