Setpoints not met

asked 2022-03-25 11:13:24 -0500

daniellosg's avatar

updated 2022-03-25 15:01:37 -0500

Hi everyone,

I'm working with a model which VRF system. I'm using detailed HVAC, and I have set the heating and cooling setpoints to 18 and 28 degrees respectively. There is no natural ventilation in the model. Occupancy is always on. However, these setpoints are not always met. See some images below:

image description

image description

I'd like the operative temperature to adjust as accurately as possible to the heating and cooling setpoints once these are exceeded.

I have no constraint in terms of the settings of the VRF system; could anyone please tell me what can I change to meet these setpoints? Also, I have had similar problems when applying unusually higher cooling setpoints, such as 32 degrees.

Please, find attached the dsb and idf files.

DSB: https://uses0-my.sharepoint.com/:u:/g...

IDF: https://uses0-my.sharepoint.com/:u:/g...

Thank you very much in advance.

edit retag flag offensive close merge delete

Comments

I don't know the details of your controller. The usual cause of "unmet' set-point is saturated action variable (controller output). The equipment heating/cooling capacity is not enough to follow your set-points. Such case is common in real life as well. I suggest you to check action variable.

kem's avatar kem  ( 2022-03-27 13:05:36 -0500 )edit