Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Does EP automatically calculate Number and spacing of Horizontal Ground heat exhchanger trenches?

asked 2022-03-16 02:34:33 -0600

eoinfwepi's avatar

updated 2022-03-16 08:45:05 -0600

Hello, I'm studying about horizontal ground exchanger.

I used 'GroundHeatExchanger:HorizontalTrench', can decision numbers of trenches, and space between of them.

I tried to use capillary tube for ground heat exchanger, but it's simulation time take so long time.(about 6 hours)

Then I found another method that 'PipingSystem:Underground' have more detailed inputs than 'GroundHeatExchanger:HorizontalTrench', it function as horizontal trenches.

Even after reading the engineering reference and input output reference, I don't know how to set it up

Could you tell me which parts?

edit retag flag offensive close merge delete

Comments

1

@eoinfwepi based on object names you're using EnergyPlus, but are you using an EnergyPlus interface (OpenStudio, DesignBuilder, etc.)?

Aaron Boranian's avatar Aaron Boranian  ( 2022-03-16 08:44:41 -0600 )edit

@Aaron Boranian I use original EnergyPlus(IDF editor)

eoinfwepi's avatar eoinfwepi  ( 2022-03-16 09:17:02 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2022-03-16 20:03:29 -0600

EnergyPlus cannot currently size a GSHP field, but it has been requested in this GitHub issue. If you would like to see this as well, give the issue a ๐Ÿ‘. From reading the issue, it appears that there may be some ongoing work in this area but it's not clear what the current status is.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2022-03-16 02:34:33 -0600

Seen: 159 times

Last updated: Mar 16 '22