Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Turning on and off plant components using outdoor ambient temperature

asked 2022-03-09 09:33:16 -0600

TigerMoley's avatar

updated 2022-03-09 11:46:53 -0600

Hi all,

I am trying to model a hybrid heat pump system in EnergyPlus 9.2, a hybrid heat pump system is essentially an air to water source heat pump that works with a gas condensing boiler used for space heating and domestic heating water. Its operation can vary between heat pump mode, hybrid mode (heat pump and boiler) and boiler only mode depending on the outdoor ambient temperature.

The figure below shows how I have the boiler and heat pump in the SVG within the space heating loop

image description

I was wondering would anyone know how I could turn on and off the boiler and the heat pump depending on the outdoor ambient temperatures to model the hybrid heat pump systems.

For above 3 degrees Celsius I would like heat pump only mode, between 3 and -2 degrees celsius I would like hybrid mode (boiler and heat pump satisfying the heating load) and for below -2 degrees I would like boiler only mode.

I was hoping to use the class PlantEquipmentOperation:OutdoorDryBulb but I think this only works for condenser equipment.

I would really appreciate any advice you all would have on this.

Thanks,

Tadhg.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2022-03-09 15:03:28 -0600

You will likely need to use an EnergyManagementSystem:Program to achieve your desired control. A similar plant control scheme based on OAT is demonstrated in the example file: EMSPlantLoopOverrideControl.idf (C:\EnergyPlusV9-2-0\ExampleFiles). Also refer to the EMSApplicationGuide.pdf documentation for more information on creating EMS programs.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2022-03-09 09:33:16 -0600

Seen: 190 times

Last updated: Mar 09 '22