Optimization of Temperature Setpoints in Energy Plus

asked 2022-02-28 10:15:40 -0600

cmm's avatar

updated 2022-02-28 14:29:35 -0600

I want to optimize the hourly temperature thermostat setpoints of an EnergyPlus idf model given a price of electricity at each hour. In other words, the goal is to minimize the cost of electricity by adjusting the setpoint temperatures at each hour.

Is this possible using GenOpt or something like that? I've been looking into GenOpt but can't seem to do optimization of hourly variables.

edit retag flag offensive close merge delete

Comments

@cmm what are you trying to optimize? It sounds like minimum annual or peak energy cost. Also, are you looking to optimize the hourly temperature setpoints of thermostats in zones or supply air/water temperatures supplied by central systems?

Aaron Boranian's avatar Aaron Boranian  ( 2022-02-28 13:17:58 -0600 )edit

Yes, minimum energy cost. The variables would be the hourly setpoint temperature of the thermostats in the zones. In my case, same temperature setpoint for all zones of a single story residential house but varies by hour.

cmm's avatar cmm  ( 2022-02-28 14:28:17 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2022-02-28 17:56:00 -0600

If you set up the set point schedule in the EnergyPlus idf file as an EnergyPlus schedule, you can override each set point value from GenOpt.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer