Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Peak cooling load - equest

asked 2021-12-30 04:16:35 -0600

udhai27's avatar

updated 2022-01-05 10:11:33 -0600

Hi all, I'm getting a peak cooling load of 10546 KBTU/HR (SS-D report), but having a cooling capacity of 21.404 MBTU/HR (PV-A report), which means only less 50% of capacity is being the peak load? is this normal or having any issue. Kindly help me in this doubt, thanks in advance.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2022-01-05 23:09:36 -0600

bfountain's avatar

If you leave your circulation loop sizing as the default "secondary" then it adds up all of the maximum coil loads at full air flow with sizing factors as the loop capacity. This often leads to the significant oversizing you describe.

An alternative is to set the loop sizing to "primary". In that case it will use the combined capacity of the primary equipment as the loop capacity. This does force you to explicitly define the the boiler or chiller capacity.

edit flag offensive delete link more

Comments

Hi, Brian Fountain thank you for your valuable input Have tried changing the loop sizing as per the peak load, now the cooling capacity increased by 2 MBTU/HR (PV-A report). Having one basic doubt, in total cooling capacity should we need to add both chilled water loop and condenser water loop capacity (PV-A report)?

udhai27's avatar udhai27  ( 2022-01-06 23:49:30 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-12-30 04:16:35 -0600

Seen: 413 times

Last updated: Jan 05 '22