Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

How can I change the air distribution effectiveness number in openstudio?

asked 2021-12-20 15:00:02 -0600

Rwadhwa910's avatar

updated 2022-02-18 17:06:02 -0600

Where can I change the air distribution effectiveness number in openstudio? I want Ez to be 0.8 during heating and 1 during cooling how can I do that?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2021-12-22 07:00:18 -0600

Petros Dalavouras's avatar

updated 2021-12-22 08:32:26 -0600

On the thermal zones tab you can choose the cooling and heating sizing parameters subtabs. There you will find the Design Zone Air Distribution Effectiveness either for cooling or heating. See also the attached picture. In the translation you will create a DesignSpecification:ZoneAirDistribution object

edit flag offensive delete link more

Comments

Thanks I found it.

Rwadhwa910's avatar Rwadhwa910  ( 2021-12-22 09:33:07 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2021-12-20 15:00:02 -0600

Seen: 280 times

Last updated: Dec 22 '21