How to set the schedule on/off for hot water pump in OpenStudio?

asked 2021-12-19 23:42:45 -0600

updated 2021-12-20 10:47:07 -0600

Due to my study of solar based vapor absorption chiller, I have completed the schedule for pump on/off control (in terms of chilled water and condenser regarding thermostat of FCU). However, the hot water pump still run all periods in the year (always activate). I would like to set the on/off for hot water pump as my need. Hence, please suggest me if it possible that I use the schedule manager (valve on/off) or others which is more suitable function?

please guide me.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2023-06-27 00:01:03 -0600

Pumpkin's avatar

OpenStudio can just assign a pump mass flow rate schedule, but it is the configuration of rated mass flow rate, not an actual mass flow rate. If you want to control the schedule on/off for hot water pump, I suggest you should work on the IDF file. Using EMS (EnergyManagementSystem) to control the status.