Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Humidistat how to output Zone Setpoint for Humidification/Dehumidification ?

asked 2021-12-08 12:56:39 -0600

mdengusiak's avatar

updated 2021-12-08 13:22:50 -0600

ZoneControl:Humidistat, Zone 2
Humidistat, !- Humidistat Name
EAST ZONE, !- Zone Name
Min Rel Hum Set Sch,
!- Humidifying Relative Humidity
Setpoint SCHEDULE Name Max Rel Hum
Set Sch; !- Dehumidifying
Relative Humidity Setpoint SCHEDULE
Name

I can set up Humidistat as above, I am trying to find an equivalent for Humidistat. I can output Setpoint for Thermostat see below:

Zone Thermostat Heating Setpoint Temperature
Zone Thermostat Cooling Setpoint Temperature

is there an option for Setpoint for Humidistat, I would expect

Zone Humidistat Humidification Setpoint Humidity
Zone Humidistat Dehumidification Setpoint Humidity

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2021-12-08 22:27:14 -0600

It doesn't look like there is an output variable for Zone Humidistat Setpoint, which is surprising.

Alternatively you can output the hourly schedule values for those RH setpoint schedules:

Output:Variable,Min Rel Hum Set Sch,Schedule Value,hourly;
Output:Variable,Max Rel Hum Set Sch,Schedule Value,hourly;