Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

VAV Reheat with Humidifer

asked 2021-12-05 00:24:01 -0600

Cold wong's avatar

I'm modeling humidity control of Data Center in Office Building. RH need to be controlled as 40%~60% in Data Center, 50% and lower in other zones occupied. A VAV reheat system control every floor, for 5 zones occupied, and 1 data center. Desiccant system has been set in every VAV airloop to dehumidification, but for terminal, only one zone(data center) need humidifer, but when I put it after reheat coil of data center, some errors occured. So how can I reach this target?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2021-12-05 08:43:24 -0600

EnergyPlus can model 17 different types of air terminal units, but they are all preset for specific configurations (reheat vs. no reheat, constant volume vs. variable volume, etc.). None of these configurations include a humidification coil. Also, the Engineering Reference section for humidifiers doesn't mention any limitations on where they can be placed (central air system, outdoor air system, single-zone HVAC, etc.).

So, you're options are to:

1) Place a humidification coil at the outlet of the air terminal unit. The outlet node from the humidification coil is now the inlet/supply node for the zone. It sounds like you have already tried this.

2) Instead of placing the humidifier after the terminal, use a single-zone HVAC component in EnergyPlus that can contain a humidifier. It would then humidify "in parallel" to the VAV system supply air. I found one for containing a dehumidifier, but not a humidifier.

3) If those both don't work, place the humidifier in the central air system serving the data center. If the other occupied zones on the same floor as the data center don't need a humidifier, then you can create a separate VAV airloop for the data center on each floor.

edit flag offensive delete link more

Comments

Thanks, that's what I'm looking for.

Cold wong's avatar Cold wong  ( 2021-12-05 08:46:25 -0600 )edit

I want to konw if EnergyPlus could simulate two AirLoops in one zone, if not, is theZoneHVAC:EvaporativeCoolerUnit a good choice?

Cold wong's avatar Cold wong  ( 2021-12-05 08:56:23 -0600 )edit

Yes, EnergyPlus can simulate multiple air systems serving one zone. You can read more in this post.

Aaron Boranian's avatar Aaron Boranian  ( 2021-12-05 18:35:43 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-12-05 00:24:01 -0600

Seen: 574 times

Last updated: Dec 05 '21