Extraneuous PIU system central heat coil output
Hi all,
I am modeling a PIU system w/ a water-cooled DX coil and series electric FPBs; no central or preheat heating coils. Using eQ v3.64, but have also observed this in eQ v3.65.
SV-A report indicates heating capacity for system is 0.
Despite this configuration, hourly reports of for SYSTEM, 'Total central heat coil output (Btu/hr)' indicates there is varying amount of central heat energy output in the first 1-2 and in some cases, the last 2-3 hours of many days in heating months (location Seattle, WA). This is also confirmed by looking at the difference in energy reported between SS-A Heating and SS-B Zone Heating. It is not necessarily a trivial amount of energy, ~10-25% of total system heating in two models I've tested.
Have others observed this before, and if so, found a way to fix this?
Can't say I've tried everything I can think of, but this is what I have tried:
- Specify HEAT-SOURCE = "NONE" and leave HEAT-SET-T undefined
- Set HEAT-SOURCE = "ELECTRIC" and use a very small capacity both -1 or -1000
- 2 + setting HEAT-CONTROL = "CONSTANT"
- 3 + set HEAT-SET-T various values, including minimum (50F)
- Setting HEATING-SCHEDULE to something that locks out heating. This works, but also locks out zone heating, so not a viable solution.
Thanks in advance for any input.