fan power input in openstudio

asked 2021-09-22 07:23:15 -0500

Lee Gyoung's avatar

updated 2022-02-21 20:48:10 -0500

Hey all. Is there a way to input fan BHP, kW, or kW/CFM in OpenStudio/energyplus? When trying to update a Packaged Rooftop VAV supply fan through OpenStudio the only fields i'm seeing are Fan Efficiency, Pressure Rise, and Motor Efficiency.

how can i solve this problem

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
1

answered 2021-09-22 10:39:29 -0500

If you use the Fan:SystemModel object, which is supposed to replace many of the other EnergyPlus fan objects in the future, you can set the Sizing Method to "PowerPerFlow" and then enter the Power per Flow Rate in units of W/m^3.

edit flag offensive delete link more
0

answered 2021-09-22 08:31:14 -0500

obuchely's avatar

I think you can not input directly fan BHP, kW or kW/cfm.

Check this post:

link text

edit flag offensive delete link more

Comments

It cannnot open the spreadsheat. that is main problem