Power Capacity control at each time step in EnergyPlus

asked 3 years ago

xavfa's avatar

updated 3 years ago

Hi to all, I am struggling to find a quick and easy way to control the power capacity (either heating or cooling) of a building at each time step, using EnergyPlus. I am not considering any specific system, so the IdealLoad's object suits me well on this. It has a parameter to limit the power, but as far as I've investigated, I couldn't find a way to make this parameter being controlled by a schedule, actuator or EMS variables. Does anybody know how to make this parameter changeable ? And if not possible using IdealLoads model, what models would be the best to enable the power capacity to be controlled ? Thanks in advance for any help on this Xavier

Preview: (hide)

2 Answers

Sort by » oldest newest most voted
1

answered 3 years ago

If you really need to control only a htg/clg power supplied to a space, you can use an OtherEquipment obj and then control the EMS actuator

EnergyManagementSystem:Actuator Available, *,OtherEquipment,Power Level,[W]

You can set convective/radiant fraction to simulate some kind of terminal units;

positive numbers stand for heat gain to the zone --> heating like

negative numbers stand for heat losses to the zone --> cooling like

Ag

Preview: (hide)
link
1

answered 3 years ago

You could indirectly control the capacity with these actuators. Controlling the mass flow rate and supply temperature/humidity effectively controls the capacity.

Preview: (hide)
link

Comments

Thanks a lot for tips ! @bonnema, may thanks, I've search for controlling either mass flow or Temp as it leads to the same effect indeed, but I didn't knew/catch that these could be controllable with actuators ! I will dig into this option. Thanks. @Ag, thanks for the workaround, but the IdealLoad still have options that are useful. I still need to represent a lot of possible HVAC systems in an automatic way (fully exhaust, balanced, with or not heat recovery, all with the same scripts and avoiding making if/then/else everywhere).

xavfa's avatar xavfa  ( 3 years ago )