Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Sudden Increase or Decrease in indoor air temperature in energyplus

asked 2021-08-19 20:31:14 -0500

Melina's avatar

updated 2022-02-24 14:36:54 -0500

Hi everyone. I have a residential building in Energyplus and the setpoint and setback are 22C and 18C for the heating season( I have 2 zones- one master and a slave). This case is in Ottawa(Canada) and because I've set the flows on Autosizing I have to define System: sizing Just from looking at similar cases in a cold climate, I set them like this: Preheat design temp.= 7C, Central heating design supply are temp.= 40 The result of flow rates are: maximum supply fan flow rate: 0.8 m^3/s,m maximum flow rate of the main zone: 0.7 m^3/s The problem is that when I open the variables file in excel I see a significant rise of temp. of the zones (specially the main zone) from set back to set point! for example, I have defined setpoint 18C from 10 pm until 6 am when people are asleep. Then I have defined the setpoint on 22 from 6 am to 9 am and then again on 18 when they are at work until 6 pm. the result is that in 6:30 the temp. is 18 and in the next time step (10 minutes later) the temp. of the main zone is about 19.4!! and in the next 10 minutes, it is 20 and then 20.5 and it does not reach 22 until 9 am! What is the reason for this strange high rising in temp. very immediately, and then it slows the process? What is wrong here?

And the more strange thing is that the temp. drops significantly from 21.5 at 9 am to 19 at 9:10 am when the people leave the house!! (I have defined no cooling for the heating season and cooling coil consumption is zero in results) and then from 19 to 18.6 for the next time step and the difference reduces as the time pasts!!!

edit retag flag offensive close merge delete

Comments

You may want to look at the scheduled internal gains from people, lights, other equipment, as well as ventilation

Ag's avatar Ag  ( 2021-08-20 14:37:28 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2021-08-21 14:07:39 -0500

It sounds like you have a model with very little internal mass. You can add internal mass objects directly to model items inside a home like furniture. Check your constructions, often a floor or foundation can provide "mass" to a model. You could also utilize the zone capacitance multiplier to add some damping effect to mimic air mixing or "real-world" inside behavior.

edit flag offensive delete link more

Comments

thank you very much for your help. The zone capacitance multiplier did work! and now the mean air temp. of each zone seems more reasonable!! Thanks a lot.

Melina's avatar Melina  ( 2021-08-24 16:41:54 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2021-08-19 20:31:14 -0500

Seen: 195 times

Last updated: Aug 21 '21