Unreasonable setting of Approach in HVAC:Template:Plant:Tower
When we use HVAC:Template:Plant:Tower
or HVAC:Template:Plant:Tower:ObjectReference
, the expidf file automatically sets condenser water temperature reset control by SetpointManager:FollowOutdoorAirTemperature
as follows:
SetpointManager:FollowOutdoorAirTemperature,
CHWloop CndW Temp Manager, !- Name
Temperature, !- Control Variable
OutdoorAirWetBulb, !- Reference Temperature Type
0, !- Offset Temperature Difference
80, !- Maximum Setpoint Temperature {C}
5, !- Minimum Setpoint Temperature {C}
CHWloop CndW Supply Setpoint Nodes; !- Setpoint Node or NodeList Name
I think Offset Temperature Difference
can be regarded as "Approach" of cooling tower. It's set to 0°C, which is unachievable in principle. A quite large range of Minimum Setpoint Temperature
and Maximum Setpoint Temperature
is also unnatural.
As mentioned in this post, cooling tower is controlled to deliver an unachievable approach of 0°C, and therefore we get high fan energy consumption. When I use HVACTemplate, I always edit expidf file to change this SetpointManager:FollowOutdoorAirTemperature
setting.
Is there any reasonable reason why Offset Temperature Difference
is set to 0°C by default? I may have overlooked something.
You haven't overlooked anything. It definitely shouldn't be 0°C for real world applications. It's done on this line https://github.com/NREL/EnergyPlus/bl... The Energy+.idd could use a default for the numeric field too. I suggest making it an enhancement request on https://github.com/NREL/EnergyPlus/is...
Thank you for your comment. I'm a little relieved to hear that. I'd like to post a request later. It would be great if
HVACTemplate:Plant:ChilledWaterLoop
had Condenser Water Temperature Reset fields, as well as Chilled Water Setpoint Reset fields.