TRNSYS_Heat Pump and Battery Bank

asked 2021-07-09 04:05:33 -0600

Claude's avatar

updated 2021-07-09 16:39:22 -0600

Hi, Is it possible to model a heat pump in Trnsys that is electrically powered by a storage battery recharged by a PV/T system? If so, how can this model be implemented? Thank you to those who can give me guidance.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2021-07-12 10:53:19 -0600

Tim McDowell's avatar

The typical heat pump models in TRNSYS take a control signal and the entering conditions and calculate the leaving conditions and the input power required. That power could be 'removed' from battery storage and the amount of additional power needed from the grid calculated. If you want to reduce the heat pump capacity based on the available power in the battery, then you will need to rewrite the heat pump model to take power as an input. This might be more difficult that it sounds since the data files used to model the heat pump performance are not set-up to provide coverage of the heat pump performance based on changing input power.

edit flag offensive delete link more