Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Reporting Carbon Dioxide levels in a space

asked 2014-10-17 12:29:37 -0600

updated 2015-07-11 20:12:58 -0600

Does anyone know how to report out CO2 levels in a space in EnergyPlus, I am sure there is a way but I can't find the output variable for it. It is a simple space with only natural ventilation and no mechanical conditioning. The space will have 300 occupants and the client wants to check CO2 levels in the space at various times. Is it enough just to specify the people or do I also need to use the "ZoneAirContaminantBalance" object to report out the CO2 levels?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2014-10-20 09:31:22 -0600

Archmage's avatar

You need to include the ZoneAirContaminantBalance input object. The output variables will not get created unless the program is actually doing the CO2 balance calculations. Then you will find the "Zone Air CO2 Concentration [ppm]" output variable.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2014-10-17 12:29:37 -0600

Seen: 568 times

Last updated: Oct 20 '14