OpenStudio Cooling Load is Zero
I'm running into this problem with a more complex OpenStudio model, but I've replicated the problem in a simple one-zone model. As far as HVAC goes, all I've done is make an air handling unit with two fans and water coils connected to district heating and district cooling. Its temperature is managed by a scheduled setpoint manager set a constant 12 C. The zone is served by the AHU with a VAV reheat. The zone's cooling setpoint is 21 C and the zone's heating setpoint is 20 C. The model runs, but only shows results for heating; no cooling. Perhaps there is a setting somewhere preventing the building from turning on cooling?
I would look at the water coil heating and cooling energy variables (COIL SPECIFIC) (look in the .rdd file to find a list of the ones you may need). Check if the water coil cooling energy is 0, since this may indicate that there is no cooling energy from the coil to the air in the air loop. In other words, the water coil is never extracting any heat energy from the air.
The water coil is connected to a plant loop on the demand side, serving an air loop on the supply side to condition air before delivering it to the zone.