Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Swapping Unitary Water cooling coil with the DX coil

asked 2021-05-18 02:37:18 -0600

Debayan93's avatar

updated 2021-05-25 12:11:09 -0600

Hi,

I am looking to connect an unitary DX Cooling coil with 2 stage Humidity control to existing CHW loop in a VAV HVAC template where I initially replaced the Unitary Water cooling coil with the DX coil. However, after deleting the unitary water coil and adding the unitary DX coil, the ''Connect Components" does not work. In case without connecting the CHW loops to AHU, it runs into simulation error.

I am currently using DB v6.1.6. I don't know if it's a exiting issue to resolve or any other I way I can solve the swapping of the coils which is mentioned in DB help file:

https://designbuilder.co.uk//helpv4.7...

I am looking if anyone has done it previously which handles the upper relative humidity control in improved way. Following in the attached is what I am looking to achieve (The red marked coil I am looking to swap as mentioned).

HVAC Template

Best,

Debayan

Edit1: I have added the new HVAC after deleting the CHW and Condenser loops. Modified HVAC Template after Deleting Loops

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2021-05-21 05:22:49 -0600

jan stasek's avatar

The DX coil does not require a connection to CHW Loop. If you replace the Water cooling coil with a DX coil, you have to delete the CHW Loop and Condenser Loop as well. You can´t have a loop without a connection.

edit flag offensive delete link more

Comments

Hi jan,

I deleted both the loops after which the leads me to the following error:

Error in HVAC definition: Humidity setpoint manager for unitary coil must be defined on the same node as temperature setpoint manager.

I have added the updated HVAC in the original question.

Debayan93's avatar Debayan93  ( 2021-05-25 12:08:28 -0600 )edit

You have to add an extra setpoint manager next to your schema's existing temperature setpoint manager and set the dehumidification control mode.

jan stasek's avatar jan stasek  ( 2021-05-25 13:44:34 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-05-18 02:37:18 -0600

Seen: 473 times

Last updated: May 25 '21