Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Relative Humidity Value Record By EnergyManagemetSystem:Sensor Does Not Match With Relative Humidity Value of System Node Relative Humidity

asked 2021-04-27 02:24:59 -0600

tri.ton99's avatar

updated 2021-04-27 02:30:22 -0600

Hi everyone,

I used EMS:Sensor to record the Relative Humidity Value of Zone like below:

EnergyManagementSystem:Sensor,
 WestZoneRH,
 West Zone Air Node,
 System Node Relative Humidity;

However, when I print the Output Relative Humidity like below and these values did not match with each other in the same timesteps (example: 20.88% vs 22.52%, 15.68% vs 16.5%, etc. Sometimes it different about 5%). When I record the temperature of the Zone by EMS: Sensor, the values were matched.

Output:Variable,West Zone,Zone Air Relative Humidity,timestep;

Output:Variable,West Zone Air Node,System Node Relative Humidity,timestep;

Can someone find where the problem is and give me some advice?

Thank you for all your supports.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2021-04-27 09:54:00 -0600

Try requesting the Output:Variables with a reporting frequency of "detailed" instead of "timestep", since the latter may be providing an average value over HVAC/system timesteps. See the Output:Variable documentation as well as the engineering documentation on EnergyPlus timesteps for more information.

edit flag offensive delete link more

Comments

Thank you for the answer.

tri.ton99's avatar tri.ton99  ( 2021-04-28 03:15:55 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-04-27 02:24:59 -0600

Seen: 179 times

Last updated: Apr 28 '21