Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

HHW pump running even when boiler is off

asked 2021-04-13 16:06:35 -0600

updated 2021-04-14 19:56:35 -0600

I am running into an issue, in OpenStudio, where the constant speed pump (intermittent control) in my HHW plant runs even when the boiler is not firing. As a result, the pump runs (cycling somewhat unpredictably) throughout the summer months, causing the HHW loop to continuously heat up - I assume due to waste heat from the pump.

I don't fully understand how the controls work by default, but I would assume that if there is a demand for heating at a coil, the pump runs, and then the boiler fires to maintain loop temperature (?). This would mean that something is telling the pump that there is a demand for heating; however, after assessing zone temperature, I can't see why that would be. Is there any basic troubleshooting around this issue (e.g. don't set the controls to intermittent)? Or, as a worst case scenario, is there some way I can force the pump off during summer months using an availability manager?

Thanks!

Hot Water Loop Plot

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2021-04-13 17:13:55 -0600

The availability manager for your HHW plant is specified in the Plantloop object. You can modify the availability managers to turn off the entire plant (including pumps). Alternatively, you can modify the availability managers controlling the airside systems, as I suspect this summer cycling is caused by airside equipment calling for heating during that period.

edit flag offensive delete link more

Comments

Thank you. You're right - it is to do with airside. Looking at it more closely, I see that during summer the pump is only operating overnight (likely when outdoor air temps are too low), but is off, as expected, during the day.

jbatt's avatar jbatt  ( 2021-04-14 08:07:03 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-04-13 16:06:35 -0600

Seen: 390 times

Last updated: Apr 14 '21