Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Does Simple Glazing System include air films ?

asked 2021-04-07 11:27:21 -0500

mval's avatar

updated 2021-04-23 08:18:59 -0500

Hi everyone,

I am using OpenStudio and the object WindowMaterial:SimpleGlazingSystem

I have calculated the overall U value with WINDOW 7.7. Do i need to enter the U value with air films in that object or should I enter the U value without the air films ?

According to the EngineeringReference the U value includes the film but when i look at the Report: Zone Component Load Summary at the section Fenestration Conduction in Estimated Heating Peak Load Components the value is lower than expected by around 20%, when the values for infiltration and exterior wall conduction are closed to what expected.

I have noticed that the value in Fenestration Conduction varies with the wind speed value in the design day so i guess the issue comes from the air films. Or is there something else ?

Thanks for your help

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
6

answered 2021-04-07 16:42:51 -0500

Keigo's avatar

updated 2021-04-07 22:37:49 -0500

The U-value in WindowMaterial:SimpleGlazingSystem includes air films, but it's just a rated value. In simulation, actual wind speed in the weather data is used. And according to Engineering Reference, the wind speed is also adjusted by the building height.

Please refer to WindowMaterial:SimpleGlazingSystem section in Input Output Reference. It says the U-Factor is the rated (NFRC) value for U-factor under winter heating conditions.

According to ANSI/NFRC 100, the rated (NFRC) value for U-factor under winter heating conditions are as follows.

image description

image description

The wind speed is 5.5m/s, resulting in the exterior convective film coefficient of 26W/m2K. (The formula used here is h=4+4V. 4+4*5.5=26W/m2K.)

I think if your model is located at wind speeds greater than 5.5 m/s, or if the height of your model is quite high, the actual U-factor used in energy simulation can be higher than the U-factor you entered in WindowMaterial:SimpleGlazingSystem. Conversely, if the wind speed is lower than 5.5 m/s, then the actual U-factor can be lower than the entered U-factor.

Please note that Input Output Reference cautions against using WindowMaterial:SimpleGlazingSystem. "There may be significant differences in performance between the simple window system and the user more detailed model."

edit flag offensive delete link more

Comments

Thanks Keigo for your quick and detailed answer. I will look into it, maybe the shape and orientation of my building impact the wind speed which improves the overall U of my fenestration.

mval's avatar mval  ( 2021-04-09 08:36:12 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-04-07 11:27:21 -0500

Seen: 241 times

Last updated: Apr 22 '21