Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Can I model a cold storage room using absorption chiller?

asked 4 years ago

maria123098's avatar

updated 4 years ago

Is it possible to model a cold storage room using refrigeration object and absorption chiller in EnergyPlus?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 4 years ago

Typically, refrigeration systems are modeled with a combination of Refrigeration:Case and Refrigeration:CompressorRack objects. This is how walk-in freezer/cooler and refrigerated display case systems are modeled in the Hospital, RestaurantFastFood, RestaurantSitDown, SchoolPrimary, and SchoolSecondary Commercial Prototype Building Models. There are other ways of modeling refrigeration systems, including Refrigeration:AirChiller and ZoneHVAC:RefrigerationChillerSet (see ExampleFiles), but I don't believe any of these objects support absorption chillers.

Depending on the zone load and the setpoint temperature that your cold storage room needs to maintain, it may be possible to serve the room with an air system that utilizes chilled water from an absorption chiller (similar to a CRAH), but this would probably be classified as a special air handling system rather than a refrigeration system.

Preview: (hide)
link

Comments

That what I concluded also from my research, so I'm trying to get it done with a simple air handling unit. But I'm not sure how I can model the products inside the room, is InernalMass object sufficient for this purpose?

maria123098's avatar maria123098  ( 4 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 4 years ago

Seen: 202 times

Last updated: Feb 01 '21