Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

how can i get inlet and out let air temperature of the cooling coil in energyplus

asked 2021-01-28 10:50:42 -0600

sara's avatar

updated 2021-03-28 09:23:04 -0600

Hi all, there is a temperature node for inlet and outlet air temperature in cooling coil part in energy plus. in the out put file i got result for temperature node. based on the result the inlet and outlet air temperature of the cooling coil is constant in winter. Also in heat pump cooling coil in large office building the supply air is from data center and the inlet air temperature in cooling coil i constant about 27c. would you please guide me n this issue. i am not sure my result is correct or not

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2021-08-23 14:49:48 -0600

Aly ElHefny's avatar

To view the temperatures at the inlet and outlet of the cooling coil you can output the variable: "System Node Mass Flow Rate" for the inlet and outlet nodes. In case you want to declare/change setpoint of supply air temperature you might want to use setpoint managers. For the zone load control, you might want to use Zone HVAC controls and thermostats.

The question is not clear but hope this helps !

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-01-28 10:50:42 -0600

Seen: 448 times

Last updated: Aug 23 '21