First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Can DOAS AirLoop flow rates be scheduled?

asked 4 years ago

Abarker's avatar

updated 4 years ago

We are trying to model a dedicated outdoor air system that modifies its flow based on a time of day schedule.

By adding a fractional schedule to the Maximum Fraction of Outdoor Air Schedule Name in the Controller:OutdoorAir object, this achieves the desired reduction in outdoor air. However, the flow in the AirLoop itself does not change and the system becomes a recirc systems at hours where the max OA fraction is scheduled to be less than 1.

As a result we don't see the fan power savings we expect, and also now have to contend with recirc air which isn't real. Is there a way to get the whole air systems flow rate to follow our fractional schedule?

Preview: (hide)

Comments

@Abarker it sounds like you are using EnergyPlus, but are you using one of its interfaces (DesignBuilder, OpenStudio, etc.) to create and edit the EnergyPlus model?

Aaron Boranian's avatar Aaron Boranian  ( 4 years ago )

Attaching your sample file (idf or whatever format you have) would also be helpful to describing the system you're modeling.

Yueyue_Zhou's avatar Yueyue_Zhou  ( 4 years ago )

Hi @Aaron Boranian, the model geometry was built using the OS SketchUp plugin and then edited further in IDF editor. All HVAC objects start as HVACTemplate and are then modified / refined further as needed.

Abarker's avatar Abarker  ( 4 years ago )

1 Answer

Sort by » oldest newest most voted
2

answered 4 years ago

Maximum Fraction of Outdoor Air Schedule doesn't change airflow in the loop, it just applies desired fraction of OA. As per docs indicates, "The current schedule value is multiplied by the current system mixed air flow rate to set the maximum outdoor air flow rate. This schedule is applied after all other limits (except EMS and demand-limiting overrides)." If you want a 100% OA system it should be 1 all the time. But where the mixed air flow is specified should be modified. I cannot tell without more details of how you model it. The least case is that you can modify the airflow by actuate fan air flow rate via EMS, where you can read in your schedule (via sensors) and multiply it by maximum/full air flow rate then assign the desired air flow rate to fan actuator. I haven't tried it but it looks reasonable in theory.

Good luck.

Preview: (hide)
link

Comments

Hi @Yueyue_Zhou, I believe I have now edited the original message to attach the model file but I don't see it anywhere (apologies, I'm not familiar with how to do it). Of course, to maintain 100% OA the fraction should always be 1.0, that makes a lot of sense. I just wonder if there is any other way to schedule the flow rate of an AirLoop without using EMS. Though if that is the only or best way to do it, so be it, and thank you for the suggestion.

Abarker's avatar Abarker  ( 4 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 4 years ago

Seen: 188 times

Last updated: Jan 15 '21