Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

W/CFM of fan power calculation

asked 2021-01-11 23:23:11 -0600

sashadf1's avatar

updated 2021-01-12 17:49:27 -0600

Hi,

Trying to specify the Diakin 3MXL24RMVJU in ResStock v2.2.4.

I know that the Fan motor rated output power is 122 W.

To specify fan power, I need w/cfm of airflow. However, I have airflow for three different fan settings (high, medium, and low) for both heating and cooling.

Diakin Fan Settings

Unsure which cfm I should use for the fan_power calculation.

edit retag flag offensive close merge delete

Comments

1

Ask to manufacturer what airflow rate the fan motor power refers to. I guess it refers to medium airflow rate

Ag's avatar Ag  ( 2021-01-19 13:25:13 -0600 )edit

2 Answers

Sort by ยป oldest newest most voted
2

answered 2021-03-15 14:54:49 -0600

TheEnergyTutor's avatar

rated motor power would always refer to high speed.

edit flag offensive delete link more
0

answered 2021-03-12 03:01:22 -0600

sashadf1's avatar

I ended up using medium fan cfm for heating in the denominator of my fan power calculation.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-01-11 23:23:11 -0600

Seen: 842 times

Last updated: Mar 16 '21