Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Meaning of Zone Energy Transfer in Meter Output?

asked 2015-05-14 09:41:32 -0600

Jlove's avatar

updated 2015-11-13 11:43:20 -0600

Can anyone help me interpret the following item of Energyplus meter outputs in mdd?

Output:Meter,Heating:EnergyTransfer:Zone.

Can this be understood as an amount of actual energy delivery from HVAC to a thermal zone?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
13

answered 2015-07-20 14:47:10 -0600

updated 2017-10-24 12:06:20 -0600

The short answer is yes. The long answer is that "energy transfer" data is organized on system, zone, facility, building, heating, or cooling meters.

Energy transfer meters refer to air or water energy transfer. The electric meters report electrical energy use. Meters used in a simulation are listed in the meter file (mdd). Each meter is described in more detail in the meter definition file (mtd). At the top of the mtd file is a list of all energy and electricity report variables and on which meters those variables are reported. For example one energy transfer variable shows the multiple meters where this energy data is stored:

 Meters for 306,SPACE1-1:Zone Air System Sensible Heating Energy [J]
  OnMeter=EnergyTransfer:Facility [J]
  OnMeter=EnergyTransfer:Building [J]
  OnMeter=EnergyTransfer:Zone:SPACE1-1 [J]
  OnMeter=Heating:EnergyTransfer [J]
  OnMeter=Heating:EnergyTransfer:Zone:SPACE1-1 [J]

In the above example, the Zone Air System Sensible Heating Energy is included on meter=Heating:EnergyTransfer as well as four other meters. One could infer that all zones would be included on the same heating energy transfer meter and finding this specific meter in the mtd shows that the Heating:EnergyTransfer meter contains information for each zone.

 For Meter=Heating:EnergyTransfer [J], ResourceType=EnergyTransfer, EndUse=Heating, contents are:
  PLENUM-1:Zone Air System Sensible Heating Energy
  SPACE1-1:Zone Air System Sensible Heating Energy
  SPACE2-1:Zone Air System Sensible Heating Energy
  SPACE3-1:Zone Air System Sensible Heating Energy
  SPACE4-1:Zone Air System Sensible Heating Energy
  SPACE5-1:Zone Air System Sensible Heating Energy

All energy data contained on a single meter is summarized at the bottom of the file. In this example, the energy transfer data for SPACE1-1:

 For Meter=EnergyTransfer:Zone:SPACE1-1 [J], ResourceType=EnergyTransfer, Group=Zone, contents are:
  SPACE1-1:Zone Air System Sensible Heating Energy
  SPACE1-1:Zone Air System Sensible Cooling Energy

 For Meter=Heating:EnergyTransfer:Zone:SPACE1-1 [J], ResourceType=EnergyTransfer, EndUse=Heating, Group=Zone, contents are:
  SPACE1-1:Zone Air System Sensible Heating Energy

 For Meter=Cooling:EnergyTransfer:Zone:SPACE1-1 [J], ResourceType=EnergyTransfer, EndUse=Cooling, Group=Zone, contents are:
  SPACE1-1:Zone Air System Sensible Cooling Energy

From the Input Output Reference document:

"Zone Air System Sensible Heating Energy [J]

This output variable represents the sensible heating energy in Joules that is actually
supplied by the system to that zone for the timestep reported. This is the sensible
heating rate multiplied by the simulation timestep. This is calculated and reported
from the Correct step in the Zone Predictor-Corrector module. This field is not
multiplied by zone or group multipliers. Zone Air System Sensible Heating (and
Cooling) Energy (and Rate) all report the heating or cooling delivered by the HVAC
system to a zone. These values are calculated by multiplying the supply air mass
flow rate by the difference between the supply air temperature and the zone air
temperature. This does not always indicate the operation of heating or cooling coils.
For example, cooling will be reported if the supply air is cooled due to the introduction
of outside air, even ...
(more)
edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2015-05-14 09:41:32 -0600

Seen: 1,762 times

Last updated: Oct 24 '17