How to Model Makeup Air Unit in OpenStudio

asked 2014-10-15 20:12:46 -0600

dannyllim's avatar

updated 2014-10-16 09:25:52 -0600

I am using OpenStudio 1.4 to model the HVAC system of a multi-story office building. The cooling requirements of the spaces on each floor are served by AHUs (for office spaces) and FCUs (for common areas). Fresh air or makeup air is provided by rooftop AHU units with heat pipe to the AHUs and spaces with FCUs to meet the ventilation requirements.

I understand that this configuration can be implemented in EnergyPlus using the AirTerminal:DualDuct:VAV:OutdoorAir object for the AHUs and AirTerminal:SingleDuct:SupplySideMixer object for the FCUs but these objects are not yet available in OpenStudio.

My question is if there is a workaround to set this up in OpenStudio and perhaps complete the setup in EnergyPlus if necessary. My point is to do the connections in OpenStudio which is easier to do than in EnergyPlus. Suggestions will be most appreciated.

edit retag flag offensive close merge delete

Comments

@dannylim. May want to add a topic tag like 'makeup-air' or 'outdoor-air' for search/routing purposes.

__AmirRoth__'s avatar __AmirRoth__  ( 2014-10-16 09:08:58 -0600 )edit

I added "doas" (dedicated outdoor air system) since it has been used already on this site.

Julien Marrec's avatar Julien Marrec  ( 2014-10-16 09:26:24 -0600 )edit

For this particular application, is the DOAS constant volume or variable volume?

MJWitte's avatar MJWitte  ( 2014-10-16 10:26:34 -0600 )edit

The DOAS is variable volume for this application.

dannyllim's avatar dannyllim  ( 2014-10-16 19:04:18 -0600 )edit

Note that current EnergyPlus does not support DOAS conditioned air feeding an AHU. In EnergyPlus v8.2.0 DOAS air can be supplied directly to a zone, to an FCU and to a zonal water-to-air heat pump unit.

MJWitte's avatar MJWitte  ( 2014-10-17 08:33:11 -0600 )edit

2 Answers

Sort by ยป oldest newest most voted
4

answered 2014-10-16 09:27:35 -0600

You are correct that the dual duct terminals are not available in OS, but beginning in 1.5 we have the AirTerminalSingleDuctSupplySideMixer. I know you said your model is version 1.4, so upgrading might not be an option for you. If however you want to migrate to 1.5, then to use the SupplySideMixer you add the terminal like any other, then you can drop the FCU on the terminal outlet node. All of the connections will be made for you. You must have the supply side mixer in place before you try to drop the FCU otherwise it will not be allowed inside the AirLoopHVAC topology.

For the dual duct terminal I suggest that you use one of the single duct terminals in OS. Then apply an EnergyPlus Measure to swap out the place holder terminal with the dual duct terminal. Since I expect you only need one leg of the dual duct the connections should all be in place, and the EnergyPlus measure should only need to swap one object for another.

edit flag offensive delete link more

Comments

Hi Kyle, thanks for the suggestions. I will upgrade my model to 1.5 because I also need the 2-speed cooling tower for the baseline model. Thanks also for the link to the Measure Writing Guide.

dannyllim's avatar dannyllim  ( 2014-10-16 19:28:24 -0600 )edit

I have a gas fired Kitchen MAU supplying OA directly to a zone that already has a dedicated roof top unit. Would the above approach be the best for this scenario? If so, can you further explain how to use the air terminal single duct supply side mixer object.

jstein@energystudioinc.com's avatar jstein@energystudioinc.com  ( 2015-04-03 13:54:50 -0600 )edit
1

answered 2014-10-16 09:05:44 -0600

I would recommend upgrading to OS 1.5... it has added a number of features which improve the program, and they've also added a number of additional HVAC objects that weren't in 1.4.

You'll have to build up your AHUs, or start from one of the template HVAC systems. You'll need an OA controller, coils for your heating and cooling, and a fan box, constant or variable, as well as one (or more) setpoint managers to make up the supply side of the AHU. Then on the demand side, you'll assign the thermal zones as well as a VAV box to serve each zone. The splitter/mixer objects are created automatically - they are represented by the branch split, and on the other side where the branches join again.

Again, my suggestion is to try version 1.5, you might find what you are looking for there.

edit flag offensive delete link more

Comments

Thanks for the suggestions Benjamin. I already did the AHUs and demand side. What I need to do next is model the makeup air unit or DOAS to feed the AHUs and FCUs with pre-cooled ventilation air. I will upgrade to version 1.5.

dannyllim's avatar dannyllim  ( 2014-10-16 19:47:30 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

3 followers

Stats

Asked: 2014-10-15 20:12:46 -0600

Seen: 1,666 times

Last updated: Oct 16 '14