Pumping system / Plant Convergence issue

asked 2020-12-08 18:36:47 -0500

updated 2020-12-09 07:37:58 -0500

The following configuration of cooling loops in energyplus works with just a few of warnings which I will mention (coolingload operation control and two setpoints and HX hasoperationschememodulated control):

image description

Now I want my pumps and chillers to have different sizes, but HeaderedPumps:ConstantSpeed gives identical pumps, so I decided to go with the following configuration with Pump:ConstantSpeed (only change): image description

I got plenty of these warnings, in one-day simulation, at the time that setpoint rises from 3 to 6.7:

*************  ** Warning ** HeatExchanger:FluidToFluid named HX - Iteration Limit exceeded calculating demand side loop flow rate continues.
   *************  **   ~~~   **   This error occurred 29 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.
   *************  **   ~~~   **   Max=74.812813  Min=0.616959

It seems that when the setpoint goes from 3 to 6.7, plant has fluid in supply side with temperature lower than new setpoint (6.7). So it stops working while Heatexchanger is demanding load. I don't know if it's a bug or is something I'm doing wrong. I will be grateful for any suggestion to resolve this issue.

Update: I'm trying an EMS (python) solution like below but it doesn't work:

If demand>0 & PLR1==0 & PLR2==0:
    pump1 (actuator) = ON
    pump2 (actuator)= ON
    pump1 flow (actuator)= max (internal variable)
    pump2 flow (actuator)= max (internal variable)

The conditions are right but pumps flow does not change. I don't no why!

edit retag flag offensive close merge delete

Comments

First, This is a great question. The schematics are most appreciated!

Could you try using a setpoint schedule that ramps up/down instead of abrutly going from 3 to 6.7 and vice versa? That is, do the transition in several steps over the course of an hour for example, where every Timestep you change it out a bit.

If your Timestep = 4 (15min), That would be H = 3, (H+15min)=3.925, (H+30min)=4.85, (H+45min)=5.775, (H+1hr)=6.7

Julien Marrec's avatar Julien Marrec  ( 2020-12-09 02:17:20 -0500 )edit

@Julien Marrec, Thank you. I tried ramping down the setpoint but that couldn't help. Here is a detailed output variable report of the simulation. Condition met column refers to the condition in the EMS code which I mentioned in my question. I should mention that the supply load of the primary and secondary are not equal! Maybe because of chillers' false loading...

Mehrdad Vojdani's avatar Mehrdad Vojdani  ( 2020-12-09 09:12:20 -0500 )edit