How to control the temprature of hot water storage tank in TRNSYS?

asked 2020-11-26 06:46:34 -0600

amirrezaheydari's avatar

updated 2021-04-13 10:31:31 -0600

Hello I need to control a storage tank temperatur with a controller (using a controller from TRNSYS standard library or TESS). The controler should turn ON the heater when the temperature of water falls below 50 C, and turn in OFF when it reaches to 60 C. So far,I have tried different controllers but none of them provided what I what. Any ideas which controller have this ability and how to use it?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2020-11-29 11:40:47 -0600

Tim McDowell's avatar

The aquastat controller in heating mode (Type106) with a setpoint of 55 and a deadband of 10 should give you the control signal that you want.

edit flag offensive delete link more