Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Is it possible for Openstudios to suggest/autosize HVAC systems based on heating and cooling loads ?

asked 2015-04-29 16:28:26 -0500

RMAK's avatar

updated 2020-03-10 09:51:17 -0500

Hello Everyone, I am doing my Design Project now and am carrying out an Lifecycle Cost Analysis. I was reading this research paper by Joshua Kneifel who was able to "...autosize the HVAC system to determine the smallest system that will meet the ventilation load requirements." It should be mentioned that he used EnergyPlus 3.0 to do this. I was wondering if the same could be done with Openstudios. I thought that I would change the building insulation and windows to get different heating and cooling load and then use the Openstudio software to "suggest" or "autosize" an HVAC system for me. It should be noted I have no idea about HVAC systems. Thank you in advance.

RMAK

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2015-04-30 12:31:05 -0500

By default OpenStudio creates models that utilize the autosize feature built into EnergyPlus. If you make no effort to "hardsize" EnergyPlus will automatically compute minimum systems to meet load and ventilation requirements.

edit flag offensive delete link more

Comments

Kyle is correct, and if you want to see these autosized equipment sizes, you can look in the Component Sizing section of the EnergyPlus Report, which you can pick from the dropdown on the OpenStudio results tab .

aparker's avatar aparker  ( 2015-04-30 12:41:23 -0500 )edit
3

I'd like to add a comment here about "autosizing" that seems to be mean different things in different programs. In EnergyPlus, "autosizing" means doing a Design Day calculation to derive the smallest HVAC capacities needed to adequately condition the space. In other programs like DOE-2 (eQUEST), "autosizing" means simulating the building loads for the entire run period or weather file to find the peak loads which are then used to derive the minimum needed HVAC capacities. The differences between the two approaches can be significant.

Joe Huang's avatar Joe Huang  ( 2015-04-30 13:11:48 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2015-04-29 16:28:26 -0500

Seen: 626 times

Last updated: Apr 30 '15