Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Predicted Mean Vote

asked 2020-08-25 03:10:04 -0500

Prethvi Raj gravatar image

updated 2020-09-16 17:16:18 -0500

Hi, I'm trying to understand the PMV for a typical shoe box model of an office. Here during the spring the PMV drops around -4. But, most of standard graphs that has PMV doesn't have values less then -2.5 .

Can PMV exceed -2.5 theoretically or even practical scenario ?

C:\fakepath\PMV -5.JPG

Regards, Prethvi.

edit retag flag offensive close merge delete

Comments

@Prethvi Raj which simulation tool are you using to analyze the shoe box model?

Aaron Boranian gravatar imageAaron Boranian ( 2020-08-25 09:12:49 -0500 )edit

Hey Aaron, I'm using Design builder and viewing the results in the results viewer.

Prethvi Raj gravatar imagePrethvi Raj ( 2020-08-28 06:40:29 -0500 )edit

1 Answer

Sort by » oldest newest most voted
2

answered 2020-09-15 13:03:56 -0500

You are correct that most graphs of PMV range from -3 to +3, where (hopefully) most values fall close to 0 to indicate that the occupants are comfortable instead of too cold (negative) or too hot (positive. However, the PMV can be calculated outside of this range, as you see in your Results Viewer plots you shared. From the EnergyPlus Engineering Reference on calculating occupant thermal comfort outputs like PMV:

Note for all Thermal Comfort reporting: Though the published values for thermal comfort “vote” have a discrete scale (e.g. –3 to +3 or –4 to +4), the calculations in EnergyPlus are carried out on a continuous scale and, thus, reporting may be “off the scale” with specific conditions encountered in the space. This is not necessarily an error in EnergyPlus – rather a different approach that does not take the “limits” of the discrete scale values into account.

So, if your shoebox model of an office has a combination of thermal comfort parameters that would make occupants very cold (cold mean air temperature, low clothing level, high airflow, etc.), then you could theoretically achieve PMV of -4. Practically, you want PMV as close to 0 as possible to maximize occupant thermal comfort.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

 

Question Tools

1 follower

Stats

Asked: 2020-08-25 03:10:04 -0500

Seen: 79 times

Last updated: Sep 15