Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Cooling Consumption Higher for 16SEER vs 15SEER - Beopt

asked 2020-08-12 09:01:53 -0600

khanmuh2's avatar

updated 2020-08-12 10:57:11 -0600

We are seeing a higher cooling consumption for 16SEER vs 15SEER in BEOpt with everything else being the same. Has anyone else seen this and if so how can this be explained.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2020-08-12 11:22:52 -0600

updated 2020-08-12 12:27:35 -0600

If the SEER 15 unit is single speed and the SEER 16 is two speed, and if there are ducts in unconditioned space, the SEER 16 run will have higher duct losses due to longer run times (see field testing evidence for this). You might re-run your test cases w/ ducts in conditioned space to isolate the effect of a SEER change. You should also make sure that nothing else is changing in the runs where you change SEER; for example, changing the water heater can result in different internal gains that the HVAC system would see.

There is also some similar discussion here.

EDIT:

Also, make sure you are looking at the combined result for both space cooling energy and cooling fan energy. There are built-in assumptions about when the fan efficiency increases as a function of SEER, so it is possible to see increased space cooling energy while the combined space cooling plus cooling fan energy is lower as expected.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2020-08-12 08:59:25 -0600

Seen: 264 times

Last updated: Aug 12 '20