First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

what is best way to model parking garage

asked 4 years ago

szsz's avatar

updated 4 years ago

May I know what is the best way to model underground parking garage which has opening to outdoor?
1. Is it possible to exclude garage from energy model? If so, how to set the boundary condition of above garage zone's floor? Set it as outdoor with no sun and wind exposure?
2. If it needs to be included in energy model, how to properly model the opening? Or make it as enclosed zone and set large ACH?
Many thanks for your suggestion!

Preview: (hide)

Comments

This post discusses using "air walls" to model the openings, and this post discusses using CFD to compare garage zone air temperatures to outdoor air temperatures. Do those answer your question?

Aaron Boranian's avatar Aaron Boranian  ( 4 years ago )

@Aaron Boranian, Thanks for your comment. Both posts all recommend including underground parking garage in the energy model, then can I get conclusion that it is not suggested to model garage as outdoor thermal condition?

szsz's avatar szsz  ( 4 years ago )

Correct, an outdoor thermal condition means the garage surfaces are exposed to outdoor air. That is the case for the garage wall where the opening is, but the garage floor and other wall surfaces of this underground garage are exposed to soil instead. You can read more in this post about how EnergyPlus calculates soil-contact temperatures.

Aaron Boranian's avatar Aaron Boranian  ( 4 years ago )

@Aaron Boranian, many thanks for your reply!

szsz's avatar szsz  ( 4 years ago )

@szsz great, I've combined all my comments into an answer below.

Aaron Boranian's avatar Aaron Boranian  ( 4 years ago )

1 Answer

Sort by » oldest newest most voted
1

answered 4 years ago

This post discusses using "air walls" to model the openings, and this post discusses using CFD to compare garage zone air temperatures to outdoor air temperatures.

An "Outdoors" boundary condition means the garage surfaces are exposed to outdoor air. That is the case for the garage wall where the opening is, but the garage floor and other wall surfaces of this underground garage are exposed to soil instead. You can read more in this post about how EnergyPlus calculates soil-contact temperatures.