Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Using chiller to temper WSHP loop

asked 2020-07-05 07:07:36 -0500

Nithya's avatar

updated 2020-07-05 08:54:34 -0500

Can anyone share how to use chiller that supplies 44F to temper WSHP loop to operate at 85F? I have used the following configuration and cannot get intended temperatures.

At the main WSHP loop- image description Here is HX config image description At the primary cooling loop- image description

In real life, a tempering valve would accomplish this, but as I understand that tempering valve is not a solution for such situations in open studio/energy plus.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-07-06 15:50:21 -0500

khaddad's avatar

Why not use a cooling tower to do the cooling in this case? EnergyPlus allows plant loops of type "cooling","heating", or "condenser". In your loop now you're doing both heating and cooling at the same time on the same loop. When you use a cooling tower you would not need the chiller loop anymore.

edit flag offensive delete link more

Comments

Khaddad, I need to use a chiller(~air to water heat pump) for this scenario. I am using manufacturer data to create performance of an Air to water heat pump based on PLR, COP and LWT. I believe this is not possible with tweaking performance of a cooling tower to replicate this piece of equipment and chiller comes close to this. The loop is designed to have chiller inject 44F to target 85F loop temperature.

Nithya's avatar Nithya  ( 2020-07-06 16:01:05 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2020-07-05 07:07:36 -0500

Seen: 289 times

Last updated: Jul 06 '20