Why do meters for variables in W units get ignored?

asked 2020-07-01 14:43:23 -0600

Vasco Zeferina's avatar

updated 2020-07-01 15:42:06 -0600

In my EnergyPlus model, I have created several Meter:Custum objects to sum several output variables.

Some of them [The ones that are rates and so in W units] return a warning message and the meter is ignored in the output data.

The message:

** Warning ** DetermineMeterIPUnits: Meter units not recognized for IP Units conversion=[W].
   **   ~~~   ** ..on Meter:Custom="TEST6".
   **   ~~~   ** ..requests for IP units from this meter will be ignored.
   ** Warning ** Meter:Custom="TEST6", variable not summed variable Output Variable or Meter Name="PLANT SUPPLY SIDE COOLING DEMAND RATE".
   **   ~~~   ** ...will not be shown with the Meter results; units for meter=W, units for this variable=W.
   ** Warning ** Meter:Custom="TEST6", no items assigned 
   **   ~~~   ** ...will not be shown with the Meter results. This may be caused by a Meter:Custom be assigned to another Meter:Custom.

The custom meter object:

Meter:Custom,
    Test6,                   !- Name
    Generic,                 !- Fuel Type
    *,                        !- Key Name 1
    Plant Supply Side Cooling Demand Rate;  !- Output Variable or Meter Name 1

I have used the following object to set unit conversion:

OutputControl:Table:Style,
    All,                     !- Column Separator
    JtoKWH;                  !- Unit Conversion

I would like to understand I do I get this error and the meters. Why is this? Shall I set a different unit conversion?

edit retag flag offensive close merge delete

Comments

Are you trying to convert the ESO/MTR results into IP units? This is an option in EP-Launch or it can be done using EnergyPlus command line options.

Aaron Boranian's avatar Aaron Boranian  ( 2020-07-01 15:46:23 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2020-07-02 14:34:23 -0600

lklawrie's avatar

Meters can only be created using "summed" variables (not rate variables)

This warning says it all: Warning ** Meter:Custom="TEST6", variable not summed variable Output Variable or Meter Name="PLANT SUPPLY SIDE COOLING DEMAND RATE".

FYI, I believe documentation and possibly error message will make this more clear in the next release.

Linda

edit flag offensive delete link more

Comments

Thanks. It is clear now.

Vasco Zeferina's avatar Vasco Zeferina  ( 2020-07-02 17:20:27 -0600 )edit