Does OpenStudio support Field: Design Return Air Flow Fraction of Supply Air Flow?

asked 2020-06-20 15:31:30 -0600

updated 2020-06-21 09:59:34 -0600

Does OpenStudio support Field: Design Return Air Flow Fraction of Supply Air Flow?

I have a system with less return flow than supply, so I want the autosize to size the return fan properly.

edit retag flag offensive close merge delete

3 Answers

Sort by » oldest newest most voted
6

answered 2020-10-14 14:23:43 -0600

updated 2020-10-17 10:19:24 -0600

This is supported in OpenStudio v3.1 (implemented here, courtesy of @Julien Marrec, which is now officially released.

New methods on the AirLoopHVAC object:

  • designReturnAirFlowFractionofSupplyAirFlow
  • setDesignReturnAirFlowFractionofSupplyAirFlow
edit flag offensive delete link more

Comments

You mean courtesy of me. I filed this request on GitHub. https://github.com/NREL/OpenStudio/is...

TheEnergyTutor's avatar TheEnergyTutor  ( 2020-10-16 21:45:20 -0600 )edit
2

No offense, but Julien made 22 code commits across several days to implement this. I’d say it’s courtesy of his efforts.

shorowit's avatar shorowit  ( 2020-10-17 10:04:22 -0600 )edit
1

answered 2020-10-16 21:47:26 -0600

TheEnergyTutor's avatar
edit flag offensive delete link more
-1

answered 2020-10-14 13:23:02 -0600

I do not see it listed in the SDK documentation, so it must not be supported.

edit flag offensive delete link more