Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

eQuest fan static pressure units

asked 2015-04-16 17:02:01 -0600

jkjenner's avatar

updated 2015-07-10 13:46:33 -0600

I'm attempting to model a school in eQuest and my fan energy seems much too low. In searching for the source of the low fan energy I noticed that the input screen in eQuest for AHU fan static pressure lists "Static in WG" for units, while the SV-A output report lists the units for the AHU fan in "IN-WATER."

What throws me is that the value in both is exactly the same: that is, I've entered a fan static pressue of 0.4 inches hg in eQuest, and the static pressure value which appears in the SV-A report in inches water is also 0.4.

Has anyone encountered this oddity? Anyone aware of what the source might be? I don't yet have a good grasp of how the unit conversions work between eQuest and DOE...

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2015-04-17 10:00:41 -0600

"WG" stands for water gauge, which is synonymous with inches of water. It is not "hg" or mercury.

edit flag offensive delete link more

Comments

Wowsers one of the dumbest mistakes of all time. Thanks a lot in any case!

jkjenner's avatar jkjenner  ( 2015-04-17 11:29:47 -0600 )edit

No problem! We all make them : ).

Neal Kruis's avatar Neal Kruis  ( 2015-04-17 12:40:08 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2015-04-16 17:02:01 -0600

Seen: 246 times

Last updated: Apr 17 '15