asked 2020-05-20 23:10:27 -0600

chldudwo13's avatar

updated 2020-05-21 08:30:30 -0600

Dear all,

In E+ 9.2.0, I'm trying to simulate a simple Data Center model which contains only ITE equipment in a zone.

The HVAC consists of Condenser Loop - Plant Loop (Chiller) - Air Loop - Zone

From this system, I would like to control the plant loop's pump mass flow rate [kg/s] and see how zone temperature changes.

Although I was able to control the pump mass flow rate by EMS, the zone temperature didn't change and stay at zone temperature setpoint.

To see the zone temperature variation by pump mass flow rate change, the zone SetpointManager must not operate.

Is there any methods to see the variation of zone temperature by controlling pump mass flow rate ignoring zone SetpointManager?

Any comments or suggestions will be very much appreciated.

Thank you for your time.

Best,

edit retag flag offensive close merge delete

Comments

@chldudwo13 could you include a link to your IDF so that others can help you better?

Aaron Boranian's avatar Aaron Boranian  ( 2020-05-21 08:22:20 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
0

answered 2020-05-21 12:07:21 -0600

What about the fan? It may happen that the air flow rate compensates (increasing) the reduced water flow rate