1

Put the pump On and the chiller is OFF in the same loop

asked 2020-05-20 12:57:20 -0500

sergerwehbe's avatar

updated 2020-05-20 15:25:58 -0500

Hi All, I have a chilled water Loop consists of Chiller, pump and adiabatic pipes. Can I make the chiller OFF and let the pump working (ON)? When I use the SYSTEM AVAILABILITY MANAGER, all the loop will be On or Off! how to specify which equipment from the loop to be ON or OFF? Thank you

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2020-05-21 12:38:57 -0500

What is you purpose?

With a Pump:ConstantSpeed you have the pump running even if there is no load on the loop and therefore the Chiller is Off. The Availability Manager Should be On. Be aware of the heat trafserred to the loop by the pump that could brings the temp loop over the max value and therefore causes a Fatal Error.

If you want to force the Chiller to stay Off even with a cooling load, you can use EMS forcing the Chiller branch flow to zero and all the flow to the by-pass (two parallel branches on the supply side sub-loop).

edit flag offensive delete link more

Comments

Thank you. But if I forced the chiller branch flow to zero! The flow By the pump ( pump is ON ) still pass via chiller while the chiller is OFF? I want the chiller be OFF while the pump is ON and the pump flow enter the chiller without any load from chiller!

sergerwehbe's avatar sergerwehbe  ( 2020-05-21 14:41:48 -0500 )edit

In my vision is the same. What should happen, thermodynamically speaking, with the flow passing through the Chiller turned off rather than through an adiabatic by-pass pipe?

Ag's avatar Ag  ( 2020-05-21 16:30:33 -0500 )edit

I tried it. It’s working. Thank you

sergerwehbe's avatar sergerwehbe  ( 2020-05-22 15:41:56 -0500 )edit